You'd just need to get the power lead and plug changed. Nothing wrong with that, normal when they get a damaged lead. The spec sheet (link below) says it runs on 230V, 50 or 60Hz so fine for here. Spec sheet does say it needs 20A at 230V so you'd need a 20A single phase outlet and dedicated 20A or 25A breaker to run it to full potential. This will mean 6 or 10sqmm cable as well from the breaker to the 20A outlet, depending upon how long the run is and how it is installed. You can run it on a 16A circuit but only up to 150A which is a 20% duty cycle - probably where you'd max out anyway. In this case you'll need a dedicated 15A outlet and a 16A breaker, and to do it right run 4sqmm cable to the outlet. The 20A outlet will cost about the same in any case. Clipsal sell a 20A outlet in either industrial style or a domestic style if it is indoors.
http://www.millerwel...heets/AD1-5.pdfHere is a Clipsal 56 series 20A single phase outlet:
http://www.ebay.com....=item3ccb204c71. You can also get these in a traditional looking single phase plug and socket, here is a plug with the traditional style in 20A, cannot be plugged into a normal 10 or 15A outlet as the pins are too big:
http://www.ebay.com....=item2575e8cbdc - you can buy the socket outlet to match.
Here is a 20A round pin plug to suit the first outlet:
http://www.ebay.com....=item4abcc48d4bHere is a whole gange of used 20A single phase outlets and plugs to match:
http://www.ebay.com....=item2c689f3c03